Marc Z Posted August 28, 2013 Report Share Posted August 28, 2013 Hi all, The venue I'm in has a temporary production power socket labelled as 125a 400v. Am I right in working this out as safe for 450,000W spread evenly over the 3 phases? So 110,000W per phase is fine? Thanks in advance, MZ Quote Link to comment Share on other sites More sharing options...
kyska Posted August 28, 2013 Report Share Posted August 28, 2013 Hi all, The venue I'm in has a temporary production power socket labelled as 125a 400v. Am I right in working this out as safe for 450,000W spread evenly over the 3 phases? So 110,000W per phase is fine? Thanks in advance, MZ I have no idea whatsoever what you're talking about, but, I say just go for it, what's the worst can happen? Let us know how you get on. Quote Link to comment Share on other sites More sharing options...
Paul223 Posted August 28, 2013 Report Share Posted August 28, 2013 sure 125 amp at 400 volt would be 50000 watt ? Quote Link to comment Share on other sites More sharing options...
Griff36 Posted August 28, 2013 Report Share Posted August 28, 2013 A 400v supply fitted with 125A fuses is 150kW or 50kW per phase. Dont forget PF if you are supplying reactive loads Quote Link to comment Share on other sites More sharing options...
goodo123 Posted August 28, 2013 Report Share Posted August 28, 2013 It's also important to check the supply mcb/fuses as although the socket might be marked up at that it doesn't mean the supply to the socket is. also you need to look if your going between 2 phases for 415v or 1phase and n as the socket might not be supplied with a neutral. Quote Link to comment Share on other sites More sharing options...
goodo123 Posted August 28, 2013 Report Share Posted August 28, 2013 Also note that if your using 230v the max power will be reduced. Quote Link to comment Share on other sites More sharing options...
bullet1747 Posted August 28, 2013 Report Share Posted August 28, 2013 Hi all, The venue I'm in has a temporary production power socket labelled as 125a 400v. Am I right in working this out as safe for 450,000W spread evenly over the 3 phases? So 110,000W per phase is fine? Thanks in advance, MZ 125 amp per phase Quote Link to comment Share on other sites More sharing options...
bullet1747 Posted August 28, 2013 Report Share Posted August 28, 2013 Hi all, The venue I'm in has a temporary production power socket labelled as 125a 400v. Am I right in working this out as safe for 450,000W spread evenly over the 3 phases? So 110,000W per phase is fine? Thanks in advance, MZ Wot venue you at firm I work for supply power to 90 percent of venues in england Quote Link to comment Share on other sites More sharing options...
Browning 425 clay hunter Posted August 28, 2013 Report Share Posted August 28, 2013 I have no idea whatsoever what you're talking about, but, I say just go for it, what's the worst can happen? Let us know how you get on. Best/funniest advice I've ever seen on here. Quote Link to comment Share on other sites More sharing options...