discobob Posted September 11, 2019 Report Share Posted September 11, 2019 This morning I got up to no hot water. Went down stairs to top the boiler up (we do need to replace an expansion vessel - I have pressurized it recently - the CH one) and sure enough it was doing the alternate flashing. Topped it up but the boiler started flashing both lights simultaneously - done a reset/switch on switch off with no change. Oh f@ck I thought. I have called the local approved for the boiler with nothing back yet - boiled kettles for the kids getting ready for school. Then I walked into the garage and lo and behold - it was working??? The fault for the flashing lights is blocked flue or fan fault. Any ideas as to why it would have started working (I left it flashing)?? Quote Link to comment Share on other sites More sharing options...
B725 Posted September 11, 2019 Report Share Posted September 11, 2019 Is it a WB as some have a thermistor or similar in the flue /sump that fails giving similar fault codes Quote Link to comment Share on other sites More sharing options...
discobob Posted September 11, 2019 Author Report Share Posted September 11, 2019 34 minutes ago, B725 said: Is it a WB as some have a thermistor or similar in the flue /sump that fails giving similar fault codes Its an Alpha (CB50) Still trying to get in touch with someone who will know the system - if not I think it will be a fixed price repair from BG/Homeserve/SSE 😞 Another question if you don't mind answering @B725, I said about the expansion vessel - this boiler has 2, one for CH and one for DHW. On topping up, I have water coming out of the DHW one but none out of the the CH. However, it is when the CH is on that the pressure increases and obviously discharges out but yet the vessel is at pressure (or was - will check when I get home). We haven't had an issue all over summer as the CH hasn't been on Cheers Quote Link to comment Share on other sites More sharing options...
B725 Posted September 11, 2019 Report Share Posted September 11, 2019 Are you sure you have them the right way round. When you say you have water coming out do you mean from the schrader valve? There should be no water you can only test the bag pressure with no water in the vessel. If the heating one has gone sometimes its easier to fit an external one rather than faff about changing the one in the boiler, the air pressure wants setting at 1 bar before fitting Quote Link to comment Share on other sites More sharing options...
Rupert Posted September 11, 2019 Report Share Posted September 11, 2019 4 hours ago, discobob said: This morning I got up to no hot water. Went down stairs to top the boiler up (we do need to replace an expansion vessel - I have pressurized it recently - the CH one) and sure enough it was doing the alternate flashing. Topped it up but the boiler started flashing both lights simultaneously - done a reset/switch on switch off with no change. Oh f@ck I thought. I have called the local approved for the boiler with nothing back yet - boiled kettles for the kids getting ready for school. Then I walked into the garage and lo and behold - it was working??? The fault for the flashing lights is blocked flue or fan fault. Any ideas as to why it would have started working (I left it flashing)?? an you hear fan running? has it been noisy recently Quote Link to comment Share on other sites More sharing options...
discobob Posted September 11, 2019 Author Report Share Posted September 11, 2019 We did have a bit of noise when it kicks up - remembered we have home emergency cover so I am putting it into their hands now 😁 just waiting on an engineers call Quote Link to comment Share on other sites More sharing options...