Could some-one please tell me what is the official line on the installation of the above.

 

Do I by by law have to install a high efficient condensing boiler or can I install a standard combi.

 

As far as I see it if you have no suitable way of routing the disposal of the condensate then you are permitted to install the latter.

 

I wish to have a new boiler installed and the engineer insists that if he installs a standard efficiency combi than by law he will be unable to commision it to CORGI regs as he says he could install a high efficiency unit, he has calculated a points system on the above and it comes out in the favour of the earlier option.

 

I however refute this as there is no drain nearby to route it to- I have no desire to have condensate dribbling from a pipe beside my back door all day long, which the engineer states even if so we be of no consequence or detriment to the property...

Surely as a home-owner I reserve the right to have what I want installed??

 

Please can one of the members of knowledge please officiate?

 

 

Regards

Link to comment
Share on other sites

Can he not fit a tank with internal pump to pump the condensate to drain ...surely if ther is room for the associated piping to the boiler then there should be enough room to install another 15mm pipe to a suitable stack ?? would find another installer if i was you ..condensing boilers are the way to go .

 

P.s condensate is acidic hence the reason it cannot be left to dribble...def find another installer

Edited by Andy_B
Link to comment
Share on other sites

he is simply trying to comply with the current building regulations. I believe they allow a non condensing in exceptional circumstances but I doubt your problem would be classed as exceptional. The issues are his livelihood and he is giving advice, is there no way of running it into a drain or possibly moving the boiler closer to one.

Link to comment
Share on other sites

he is simply trying to comply with the current building regulations. I believe they allow a non condensing in exceptional circumstances but I doubt your problem would be classed as exceptional. The issues are his livelihood and he is giving advice, is there no way of running it into a drain or possibly moving the boiler closer to one.

 

No, there is no chance of running to a drain at all, I don't have any exterior drains as the property is fairly new, and everything runs internally. No soil stack, no surface water drains access either.

 

Can't move the boiler either as I am not having a new hole ran through the wall for a flue as the house is too new and making good would not be cosmetically good enough.

Link to comment
Share on other sites

firstly, you dont come across the circumstances which dont allow the installation of a high efficiency boiler pretty often... theres usually somthing thats can be done...however, theres always an exception to every rule.... and when the installation cannot be done, an older standard efficiency boiler can be installed with written permission from corgi (soon to be " gas safe")..... ive never had this happen though, usually there is an answer....

 

secondly.... the guy who came out and gave you advice is right in what he says,..... if you want the installation to comply with current legislation etc, it must be H/E... as of april 2005 that was..... and i might add, youd probably have an awfull lot of trouble buying a standard effieciency boiler even if you wanted one !!! when the change over happened, installers like myself bought what the merchants had on the shelves for a low price... these were then installed on cash jobs with no paperwork...thats doesnt make the job any less a quality or dodgy, it just didnt comply with regulation...it was not to current standards... ( but, however, not allowed none the less....usally for friends and family etc...) so, anyway,i doubt youd find a new one.

 

thirdly.... the h/e boilers are very efficient and i know which way id rather go with the price of gas..... deffo h/e.

 

as for you having no drain point for your condensate.... the pipe he suggest having dripping by the door.....:good: well, you would'nt have or leave ANY condensate drain dripping, ever. they must be sleeved to protect from freezing as a frozen condensate drain will halt the operation of any boiler pronto. if you have a gulley or drain, the sleeved condensate pipe must go right into it.... IF YOU DONT HAVE A DRAIN, YOU NEED TO FITT A SOAK AWAY DRAIN...this is a small drain dig a hole around 2 foot deep and 1 foot across... put the soak away drain into it and back fill the hole with lime chippings....soil/paving etc can be re made neatly over the top... your condensate drain will now fit into the soak away.....

but usually, the condensate can be ran into a waste pipe off a bath/sink/basin/shower/washing machine or straight into a soil stack via a strap on boss..... where theres a will, theres a way.

as stated above, condensate waste is mildly acidic and has to be dealt with properly.

 

so finally... dont be so cinical , the lad was trying to do the job right for you, not push you into doing somthing you dont want or need.... you dont really have "much" choice about it....

unless of course you want to get a standard efficiency boiler and do it yourself ? or have some pleb off a six week course come round and "have a go"....

 

any questions, just ask.....

Edited by myzeneye
Link to comment
Share on other sites

I think you can put a purpose made soak away in to a depth of about 500mm , and fill with a bag of lime chips to discarge the condensate, the lime chips break down the acidic in the water , Dont quote me on it though as im a electrician not Gas engineer

 

 

beat me too it old pal whilst i was typing that load of pap out above... :good:

Link to comment
Share on other sites

I get asked this question on a regular basis as a building inspector and this is the approach most BCO's adopt,

 

as long as the new boiler is at least 86% efficient and it is not practical to run a drain to collect the condensate there is no requirement to install a condensing type boiler, generally this means digging up internal floors, if the boiler is on an external wall and an external drain could be reasonably easily extended then it would need to be done and a condensing boiler fitted, digging up lawn or flower beds would be seen as reasonable, digging up hard paved areas would not.

 

mikee

Link to comment
Share on other sites

I own an independent plumbing merchants and standard efficiency combi boilers are now more expensive that h/e. Its because the manufacturers have to stop usuall production to make one. If your lucky to find one on the shelf, REMEMBER it will now be nearly 4 years old and if it packs up there will not be any warrantee. Also average house will save around £75 per annum on gas with a condenser. Go with the advice of the pro's and go for the condensing option.

Link to comment
Share on other sites

as a gas inspector and heating engineer i have yet to see a typical domestic property that cannot have a sedbuk A or B rated boiler installed.

 

with all the different flueing options and condensate disposal options (pumped away, soakway etc.) you will find it very difficult to get an exemption

 

as it seems like you live in a newer property just remember the condense must terminate into a foul drain and not the rainwater system as the theory now is that if to much condense runs into the rainwater system it could eventually contaminate it, as it is slightly acidic

 

what boiler are you considering??

Edited by krazykayaker
Link to comment
Share on other sites

I get asked this question on a regular basis as a building inspector and this is the approach most BCO's adopt,

 

as long as the new boiler is at least 86% efficient and it is not practical to run a drain to collect the condensate there is no requirement to install a condensing type boiler, generally this means digging up internal floors, if the boiler is on an external wall and an external drain could be reasonably easily extended then it would need to be done and a condensing boiler fitted, digging up lawn or flower beds would be seen as reasonable, digging up hard paved areas would not.

 

mikee

 

that may be the case on your patch mikee... and thats good for any loon in your area who doesn't want a high efficiency appliance (:welcomeani:) but in other area's,with other more militant bco's there aint much chance of getting away with standard efficiency... there are too many alternative options,like the soak away drain.... they take a few mins to install, so no drain or gulley aint really an excuse...... ok, what if the floor out side is concrete/tarmac etc..... well how hard is it to wizz a hole out of it to sink a soak away..(core bit could make a neat hole/still saw could cut a neat square etc etc ..... if the boiler can only go in the centre of the building..... well the pumped option will get you into a nearby waste pipe in a kitchen/bathroom etc etc....

there isnt really allot of instances where installation would be deemed totally impractable....

 

me, if i was buying a boiler...i would be insisting on a h/e anyway....and would explore every option for fitting a con drain... as a last resort if it where totally impractable, well then id have to have a s/e but it would be with some reluctance....

 

where is the boiler sited now :good: where is the nearest drain/waste pipe/soil pipe etc..,.can the boiler site be moved ? i often give at least two options when siting the boiler.... existing site/old cylinder location or the favourite, in the loft....

Link to comment
Share on other sites

Firstly, the soil stack is out of sight, runs through the center of the house and all drain services are hidden form view. Most fairly new builds don't have waste pipe coming out the kitchens or bathrooms these days anyway and most run internally. No I cannot dig up my access area as I have block paving down and a soak-away is more work. Even the engineer has said he can't run the condensate to the sink waste.

 

It is just a stalemate

 

I just don't see why you have to be told what to install..... It is up to the consumer at the end of the day

 

There are some good points that the Engineers have highlighted though... The benefits of the condensing system etc which I fully appreciate.

 

I just don't like being told what to do in my own house when I am doing the paying.....

 

The reason I am replacing my boiler is that in the near future I intend to extend and the current boiler is too close to the mark and will struggle to run the additional load,

 

Current boiler potterton

 

New boiler -Worcester Bosch

Link to comment
Share on other sites

If only building control accepted it was your house and you could do what the hell you liked life would be much simpler. But fact is they don't so you either get it done on the side and don't comply but when you have your extension it is likely to be the reason they won't sign it off. If you get the wrong BCO you'll end up being forced to fit a new one or not get the work signed off at which point your house will be un saleable. Sounds very over the top but its the way it works

Link to comment
Share on other sites

If only building control accepted it was your house and you could do what the hell you liked life would be much simpler. But fact is they don't so you either get it done on the side and don't comply but when you have your extension it is likely to be the reason they won't sign it off. If you get the wrong BCO you'll end up being forced to fit a new one or not get the work signed off at which point your house will be un saleable. Sounds very over the top but its the way it works

 

What you do is run a dummy pipe from the boiler simulating condensate overflow.... Get some condensing boiler stickers on the front of the casing and away you go.

Link to comment
Share on other sites

as a gas inspector and heating engineer i have yet to see a typical domestic property that cannot have a sedbuk A or B rated boiler installed.

 

with all the different flueing options and condensate disposal options (pumped away, soakway etc.) you will find it very difficult to get an exemption

 

as it seems like you live in a newer property just remember the condense must terminate into a foul drain and not the rainwater system as the theory now is that if to much condense runs into the rainwater system it could eventually contaminate it, as it is slightly acidic

 

what boiler are you considering??

 

does the surface water from your house discharge to the surface water sewer system or to a soak away in the garden, if to a soak away and you can get to a down pipe you can run it away in there

 

mikee

Link to comment
Share on other sites

If only building control accepted it was your house and you could do what the hell you liked life would be much simpler. But fact is they don't so you either get it done on the side and don't comply but when you have your extension it is likely to be the reason they won't sign it off. If you get the wrong BCO you'll end up being forced to fit a new one or not get the work signed off at which point your house will be un saleable. Sounds very over the top but its the way it works

 

al4x, its not building control who dont accept its your house and you can do what you like to it, its the secretary of state who has decided because in his view its your house but everybody's gas reserve and environment, and who's to say you don't do all this work and then sell the place.

 

mikee

Link to comment
Share on other sites

believe me mate, i more then familair with the design and layouts of most systems, new build and old....

so, as for the soil pipe being "out of sight"...what does that matter ? surely it can be accessed at some point, and if it cant you should be able to access a waste pipe under a floor board/panel or behind a stud wall etc...if youve got a soil pipe, then its not impossible to get at it at some point....

if you wanna bake a pretty cake pal, youve gotta crack some eggs im afraid......

and if you had to install a soak away... they take minutes to install.... they're cylindrical, approx 5-6 inches in diameter and around 12 inches long.... now if you cant lift a few blocks , probably two at the most to dig down a hole with a trowel this size and drop one in and top up with lime chipps, then theres just something plain wrong.... its that simple.... they are simple to install....it would take minutes honestly.

 

i agree ,you should be able to do what the hell you please in your own home, but in this day and age with climate issues etc, the keoto agreement kicked off the initiative that any appliance install should be of a certain level of efficiency.... gas is not renewable, and weather you agree with the global warming issues or not evry one should make a conscious effort to consume more efficiently.

 

seems to me like the installer youve chosen has told you a few things which are gonna create a little more upheaval then you had anticipated and this, has put a bee in you bonnet.... well, the answer is to try a different installer..... there are ways around every problem, i deal with them day in day out....there will be a solution, if of course, your willing to have one.

 

not having a go mate, just try and be realistic about the whole thing....

 

finally, worcester bosch are ok, but my money is on vaillant. every time.

Link to comment
Share on other sites

exactly right daz, if its there, its accessible...

you may think its not, but it is... theres always a way.... when you know how that is....

 

if you think that lifting floors or opening ducts/boxes is unnecessary and will be too traumatic to add to the installation, then its a miracle worker you need, not a plumber.

your soak way is totally doable. if i turned up to an install and it had to have a soak away, i wouldnt see it as a problem at all, often its a much much easier option... the fact that you have block paving is neither here nor there and would only add approx ten min's onto the overall time it would take to install into soil.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...