Archie-fox Posted April 10, 2019 Report Share Posted April 10, 2019 morning all, so after my last post about our boiler loosing pressure, we exchanged the pressure vessel, after a day the pressure was down again so on advice of our plumber we decided to go for a new boiler and rads with new valves, as you can guess after £2500 on a new baxi boiler and rads i was more than angry to find a day later zero pressure, its loosing 1.5 bar per day so after 3 weeks if there was a leak on the system im sure we would have found a wet patch somewhere, we have checked as much piping as possible id say 80% and no leaks, the rest of the piping is under floor boards in ceiling, ive phoned the plumber again this morning and hes said, "theirs nothing i can do" and left it at that... has anyone got any ideas?? what should i do regarding the plumber just washing his hands of it? cheers for any help!! Quote Link to comment Share on other sites More sharing options...
ditchman Posted April 10, 2019 Report Share Posted April 10, 2019 check outside to see if the overflow pipe is dripping..........if it is ....the valve is not seating properly............these valves in hardwater areas are notorious for not seating properly if played with........as they are spring loaded.. Quote Link to comment Share on other sites More sharing options...
oldypigeonpopper Posted April 10, 2019 Report Share Posted April 10, 2019 (edited) 15 minutes ago, Archie-fox said: morning all, so after my last post about our boiler loosing pressure, we exchanged the pressure vessel, after a day the pressure was down again so on advice of our plumber we decided to go for a new boiler and rads with new valves, as you can guess after £2500 on a new baxi boiler and rads i was more than angry to find a day later zero pressure, its loosing 1.5 bar per day so after 3 weeks if there was a leak on the system im sure we would have found a wet patch somewhere, we have checked as much piping as possible id say 80% and no leaks, the rest of the piping is under floor boards in ceiling, ive phoned the plumber again this morning and hes said, "theirs nothing i can do" and left it at that... has anyone got any ideas?? what should i do regarding the plumber just washing his hands of it? cheers for any help!! hello, sorry to hear this Archie, is the plumber registered ? or registered with Baxi boiler Co ? go online and see if there is any feed back from previous customers, if you cannot see any leaks from pipework or wet patches on ceiling what about the boiler over flow pipe to the out side wall, ? it is very frustrating when these things happen as i know only to well, can you say what model Baxi boiler ? Edited April 10, 2019 by oldypigeonpopper Quote Link to comment Share on other sites More sharing options...
Guest Posted April 10, 2019 Report Share Posted April 10, 2019 (edited) My system has a minor leak somewhere.all I did was put a bottle of radiator seal in the system had no problems. Since . Mine used to loose its pressure overnight .have you tried that yet https://www.screwfix.com/p/flomasta-0647-central-heating-leak-sealer-500ml/6774r Edited April 10, 2019 by Guest Quote Link to comment Share on other sites More sharing options...
Archie-fox Posted April 10, 2019 Author Report Share Posted April 10, 2019 3 minutes ago, oldypigeonpopper said: hello, sorry to hear this Archie, is the plumber registered ? or registered with Baxi boiler Co ? go online and see if there is any feed back from previous customers, if you cannot see any leaks from pipework or wet patches on ceiling what about the boiler over flow pipe to the out side wall, ? it is very frustrating when these things happen as i know only to well, can you say what model Baxi boiler ? its a brand new baxi 400 boiler, nothing i can see dripping.. Quote Link to comment Share on other sites More sharing options...
oldypigeonpopper Posted April 10, 2019 Report Share Posted April 10, 2019 1 minute ago, Swinton said: My system has a minor leak somewhere.all I did was put a bottle of radiator seal in the system had no problems. Since . Mine used to loose its pressure overnight .have you tried that yet hello, not something i would do yet as the Boiler is under warranty Quote Link to comment Share on other sites More sharing options...
Archie-fox Posted April 10, 2019 Author Report Share Posted April 10, 2019 1 minute ago, Swinton said: My system has a minor leak somewhere.all I did was put a bottle of radiator seal in the system had no problems. Since . Mine used to loose its pressure overnight .have you tried that yet not as yet as the boiler and rads are a week old Quote Link to comment Share on other sites More sharing options...
Guest Posted April 10, 2019 Report Share Posted April 10, 2019 (edited) It could be a joint somewhere with just a slight leak a combi system does not hold a lot of water and does not have to loose much for pressure to drop .once the pressure drops it stops leaking .you will has a hell of a job finding it .for what it cost I would try a leak sealant . Edited April 10, 2019 by Guest Quote Link to comment Share on other sites More sharing options...
oldypigeonpopper Posted April 10, 2019 Report Share Posted April 10, 2019 4 minutes ago, Archie-fox said: its a brand new baxi 400 boiler, nothing i can see dripping.. hello, have you registered the boiler yet for warranty or did plumber do ? Quote Link to comment Share on other sites More sharing options...
LondonLuke Posted April 10, 2019 Report Share Posted April 10, 2019 If you suspect a leak then leaving the filling loop open may help you find it..... Quote Link to comment Share on other sites More sharing options...
Archie-fox Posted April 10, 2019 Author Report Share Posted April 10, 2019 2 minutes ago, oldypigeonpopper said: hello, have you registered the boiler yet for warranty or did plumber do ? the plumber said he would do that for me, worst thing is hes a friend and i feel hes led me up the garden path a little bit... 4 minutes ago, Swinton said: It could be a joint somewhere with just a slight leak a combi system does not hold a lot of water and does not have to loose much for pressure to drop .once the pressure drops it stops leaking .you will has a hell of a job finding it .for what it cost I would try a leak sealant . yea when i top it up the needle jumps from 0.5 bar to 3 bar then settles to about 1.5 bar in a second or so... Quote Link to comment Share on other sites More sharing options...
oldypigeonpopper Posted April 10, 2019 Report Share Posted April 10, 2019 3 minutes ago, Archie-fox said: the plumber said he would do that for me, worst thing is hes a friend and i feel hes led me up the garden path a little bit... yea when i top it up the needle jumps from 0.5 bar to 3 bar then settles to about 1.5 bar in a second or so... hello, oh well that is not good, anyway Archie did he fill in the Baxi boiler Benchmark commissioning checklist paper work and leave with you when he finished installing the heating system ? with this you can register the warranty online with Baxi yourself Quote Link to comment Share on other sites More sharing options...
Archie-fox Posted April 10, 2019 Author Report Share Posted April 10, 2019 2 minutes ago, oldypigeonpopper said: hello, oh well that is not good, anyway Archie did he fill in the Baxi boiler Benchmark commissioning checklist paper work and leave with you when he finished installing the heating system ? with this you can register the warranty online with Baxi yourself he took the paperwork and said he would drop it all off this week with the gas safety cert.. ill wait for the paperwork then get another plumber to give it all a once over and bill the first plumber for any further work.. Quote Link to comment Share on other sites More sharing options...
dodgy dave Posted April 10, 2019 Report Share Posted April 10, 2019 could be the automatic air valve on the boiler Quote Link to comment Share on other sites More sharing options...
oldypigeonpopper Posted April 10, 2019 Report Share Posted April 10, 2019 25 minutes ago, Archie-fox said: he took the paperwork and said he would drop it all off this week with the gas safety cert.. ill wait for the paperwork then get another plumber to give it all a once over and bill the first plumber for any further work.. hello, i would get that paperwork A S A P, you only have 30 days to register warranty from date in installation, if you go that way of a plumber checking heating my advice would be a gas heating engineer as i know from past experience, maybe there is one on PW near you ? i do hope you can get all this sorted Archie, Quote Link to comment Share on other sites More sharing options...
basset Posted April 10, 2019 Report Share Posted April 10, 2019 You haven’t got any pipework for the downstairs curcuit buried in concrete floor have you that could be leaking and won’t show . If you have had a new boiler and rads , that only leaves original heating pipework that could be leaking , I would say your heating chap has made a mistake , did he pressure test original pipework before saying you need new boiler . I would have filled boiler to 1 bar pressure turned valves off under boiler and seen if it dropped that would have ruled out exsisting boiler Quote Link to comment Share on other sites More sharing options...
silver pigeon69 Posted April 10, 2019 Report Share Posted April 10, 2019 I had this same problem for about 4 yrs! It was a tiny leak on a soldered joint, that only leaked when the pipe was hot. The drip ran down a fall on the pipe and had evaporated/ dried itself before dripping onto anything, so no wet patch. Quote Link to comment Share on other sites More sharing options...
paul1966 Posted April 10, 2019 Report Share Posted April 10, 2019 can you fit isolation valves in the pipework at various points to lock off sections and see if the leak stops. Quote Link to comment Share on other sites More sharing options...
B725 Posted April 10, 2019 Report Share Posted April 10, 2019 There is definitely a leak buts sounds like it's very small and possibly evopating so you cannot see it, Sentinal internal leak sealer won't affect the pump but finding the leak is far better to do. Quote Link to comment Share on other sites More sharing options...
Guest Posted April 10, 2019 Report Share Posted April 10, 2019 8 hours ago, Swinton said: It could be a joint somewhere with just a slight leak a combi system does not hold a lot of water and does not have to loose much for pressure to drop .once the pressure drops it stops leaking .you will has a hell of a job finding it .for what it cost I would try a leak sealant . Like I said try some leak sealant first .will not hurt any part of system Quote Link to comment Share on other sites More sharing options...
Lloyd90 Posted April 10, 2019 Report Share Posted April 10, 2019 30 minutes ago, Swinton said: Like I said try some leak sealant first .will not hurt any part of system I bet it’ll P him right off if it works though, as that’ll mean he didn’t need a £2500 new boiler in the first place!!! Quote Link to comment Share on other sites More sharing options...
figgy Posted April 10, 2019 Report Share Posted April 10, 2019 I have never liked the only fit new boiler and rads that some do. If the rads are knackered the pipework needs changing also. The solder dries out in the joints the pipes wear thin where they rub on joists and walls. If you can't find the leak try leak seal,your not looking anything by doing it. Other than that it means exposing and checking every bit of pipe. Quote Link to comment Share on other sites More sharing options...
davewh100 Posted April 11, 2019 Report Share Posted April 11, 2019 17 hours ago, basset said: You haven’t got any pipework for the downstairs curcuit buried in concrete floor have you that could be leaking and won’t show . If you have had a new boiler and rads , that only leaves original heating pipework that could be leaking , I would say your heating chap has made a mistake , did he pressure test original pipework before saying you need new boiler . I would have filled boiler to 1 bar pressure turned valves off under boiler and seen if it dropped that would have ruled out exsisting boiler i would go with this definitely sounds like a leak somewhere Quote Link to comment Share on other sites More sharing options...
Guest Posted April 11, 2019 Report Share Posted April 11, 2019 I had a extension done and 2 new rads fitted .then I got a slight pressure drop every day .had to repressure every morning.put rad seal in no problem since.was not going to rip floor up to check .not pressurerised for about 5 month . Quote Link to comment Share on other sites More sharing options...
sandspider Posted April 11, 2019 Report Share Posted April 11, 2019 Do you have UFH? Had a leak that was hard to track down, turned out to be the UFH manifold... Quote Link to comment Share on other sites More sharing options...