Radiator valve identification please


harrycatcat1
 Share

Recommended Posts

This radiator at my daughters has been on for 25 + years and has been covered up with a radiator cover for a long time. It has not got warm for I don't know how long. She's on holiday so I decided to take the radiator cover off and bleed it. I turned the heating on and the pipes leading to the radiator get hot but not the radiator.  The valve is turned on so I'm assuming that the valve is full of muck. In my wisdom I tapped it to see if I could loosen anything but it started leaking so put a bowl underneath and ceased work.  It's now stopped dripping.  The plumber is coming next week but I thought if I could identify the valve and get one it would save him time chasing about.

 

Screenshot_20220827-110832_Gallery.jpg

Screenshot_20220827-110839_Gallery.jpg

Screenshot_20220827-110848_Gallery.jpg

Screenshot_20220827-112245_Gallery.jpg

Edited by harrycatcat1
Link to comment
Share on other sites

Twin entry valve the return inside the valve has a length of pipe two thirds into the radiator, they stopped making them year's ago, rubbish when new never mind now. Only solution is to fit two new valves they usually are 8mm but a few were 10mm.

Microbore heating was a quick and cheaper way of installing heating but very really done correctly. 

Link to comment
Share on other sites

Change the radiator but fit 15mm radiator valves then reduce down to the pipe size it makes it a bit easier if you have to change the valve in the future, it also gives a slightly better flow rate through the valves as there is slightly less restriction. 

Link to comment
Share on other sites

2 hours ago, B725 said:

Change the radiator but fit 15mm radiator valves then reduce down to the pipe size it makes it a bit easier if you have to change the valve in the future, it also gives a slightly better flow rate through the valves as there is slightly less restriction. 

Thank you 👍

2 hours ago, Jaymo said:

Without inspection then I would say the rad doesn’t look to be in the best condition. 
Replace with a type 21 to maintain slim profile behind the rad cover, unless space not a prob and can fit a type 22. 
 

Thank you 👍

Link to comment
Share on other sites

1 hour ago, amateur said:

The chances are that the microbore is blocked as well.

We, unfortunately, have it in our, now 30 year old, new-build. I replace it wherever I can. Awful stuff.

Well, when I put the heating on the two pipes going into the valve were very hot but the heat didn't go into the radiator. Whether rightly or wrongly I assumed that the valve was blocked.

Link to comment
Share on other sites

2 hours ago, amateur said:

The chances are that the microbore is blocked as well.

We, unfortunately, have it in our, now 30 year old, new-build. I replace it wherever I can. Awful stuff.

Our house built in the 1930s had central heating fitted in 1980 and all the pipe work to the rads is 10mm microbore, never had a days problem with it, mind you I do drain it down every couple of years and add new scale inhibitor.

Link to comment
Share on other sites

Screenshot_20220827-172941_Google.jpg.64093e7e45f9faddb9d5bdaa163e206d.jpg

If you look at the picture you can see the pipe coming from the centre of the valve and the pipe should be around 3/4 of the length of the radiator to disperse the heat across the radiator, as both pipes got hot it's just circulating through the valve, the pipe is either missing or dropped out of the centre of the valve. 

Link to comment
Share on other sites

1 hour ago, B725 said:

Screenshot_20220827-172941_Google.jpg.64093e7e45f9faddb9d5bdaa163e206d.jpg

If you look at the picture you can see the pipe coming from the centre of the valve and the pipe should be around 3/4 of the length of the radiator to disperse the heat across the radiator, as both pipes got hot it's just circulating through the valve, the pipe is either missing or dropped out of the centre of the valve. 

That makes sense 👍👍

Link to comment
Share on other sites

On 27/08/2022 at 11:43, old'un said:

I am not a plumber but I have never seen a valve with two inlets/outlets on one valve, are there any pipes on the left of the rad? the pipe looks like 10mm microbore?

 

 

One pope from the valve reaches along the radiator base to create a circulation.

 

Blackpowder

 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.
Note: Your post will require moderator approval before it will be visible.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
 Share

  • Recently Browsing   0 members

    • No registered users viewing this page.
×
×
  • Create New...